snlmdk posted this 09 March 2018

When the thresholds are set in the UPS settings | Shutdown Threshold Values, how does that relate if you have multiple UPS in the UPS list with different remaining times ?

If one of the UPS is below the threshold value, does that means that the shutdown sequence will start anyway, altough the other UPS are still above the threshold?

Cheers
Marcel

 

snlmdk posted this 13 March 2018

In the Opmonis-manual-v1.40.pdf  manual this question is answered:

Important: If you use multiple UPSs, the first time a threshold is reached by an UPS will trigger the shutdown, even if there is enough capacity left in another UPS.

Cheers
Marcel